Mixed Use Bldgs

Tom Hill

Member
Joined
Sep 8, 2010
Messages
5
We have a new bldg proposed-approx. 4,000 sq per floor

1st Floor- M/A-3

2nd Floor-B/R-2

3rd Floor -R-2

It doesn't meet the 1007.2.1 requirement but because it has R-2 on the 2nd and 3rd floors (which will require Type B units) will this project require an elevator?

1007.2.1 Elevators required.

In buildings where a required accessible floor is four or more stories above or below a level of exit discharge , at least one required accessible means of egress shall be an elevator complying with Section 1007.4.
 
It doesn't meet the 1007.2.1 requirement but because it has R-2 on the 2nd and 3rd floors (which will require Type B units) will this project require an elevator?
Yes 2009 IBC. Section 1007.2.1 sends you to 1007.4 which basically says the elevator has to be on standby power/generator

1104.4 Multilevel buildings and facilities.

At least one accessible route shall connect each accessible level, including mezzanines , in multilevel buildings and facilities.

Exceptions:

1. An accessible route is not required to stories and mezzanines that have an aggregate area of not more than 3,000 square feet (278.7 m2) and are located above and below accessible levels. This exception shall not apply to:

You have more than that
 
As I read the OP the building is 4,000 sq per floor and that would require an accessible route to all floors. The 2 ways to accomplish that would be a ramp (impractical) or an elevator

 
One of the exceptions are levels that do not contain accessible elements as determined by sections 1107 or 1108. They may not need an accessible route to the 3rd floor, only the 1st. and 2nd.
 