This has got to be a noob question, but here it goes.
I have an existing 1 floor 14,900 SF III-B building with an automotive repair facility(S-1) (Haz-mat under IBC limits) and a grocery store (M). According to 2009 IBC, the strictest use is M (12,500 SF). Assuming the building is not sprinklers (for area increase), normally I would just provide fire separation in accordance with 508.2 to provide a separated mixed use building. However the requirement is N (No Separation Required).
It reads as though any separation between the two (even a wall made of rice paper) would suffice, though the red flags are going off in my head. It really cant be that simple, can it? Right now the wall separating the two units is a 2x4 stud wall with open studs on one side.
I have an existing 1 floor 14,900 SF III-B building with an automotive repair facility(S-1) (Haz-mat under IBC limits) and a grocery store (M). According to 2009 IBC, the strictest use is M (12,500 SF). Assuming the building is not sprinklers (for area increase), normally I would just provide fire separation in accordance with 508.2 to provide a separated mixed use building. However the requirement is N (No Separation Required).
It reads as though any separation between the two (even a wall made of rice paper) would suffice, though the red flags are going off in my head. It really cant be that simple, can it? Right now the wall separating the two units is a 2x4 stud wall with open studs on one side.