First post, thank you for your input.
I am having a difficult time reconciling the provisions between IBC 2018 508.3 Non-separated Occupancies and 506.2.4, Mixed Occupancy, multi-story buildings.
Most of what I am seeing is that if the Non-separated provisions are to be used, the most restrictive aspects will apply to the entire building with respect to building area and height/stories. As an example, for a building of type VA construction with an A-3 and B spaces within, it would seem that the building would be limited to 3 stories due to the A-3 occupancy if we were to employ the non-separated provisions. Assume accessory occupancies is not an option.
However, section 506.2.4 states that "Each story of a mixed occupancy building with more than one story above grade plane shall individually comply with the applicable requirements of 508.1" Does this mean the building could be 4 stories and employ 508.3 as long as the A-3 space was not located above the 3rd floor?
Thank you!
I am having a difficult time reconciling the provisions between IBC 2018 508.3 Non-separated Occupancies and 506.2.4, Mixed Occupancy, multi-story buildings.
Most of what I am seeing is that if the Non-separated provisions are to be used, the most restrictive aspects will apply to the entire building with respect to building area and height/stories. As an example, for a building of type VA construction with an A-3 and B spaces within, it would seem that the building would be limited to 3 stories due to the A-3 occupancy if we were to employ the non-separated provisions. Assume accessory occupancies is not an option.
However, section 506.2.4 states that "Each story of a mixed occupancy building with more than one story above grade plane shall individually comply with the applicable requirements of 508.1" Does this mean the building could be 4 stories and employ 508.3 as long as the A-3 space was not located above the 3rd floor?
Thank you!