We often see DIY people doing their own work and mixing 14 & 12 on the same circuit and we have to tell them they must be on a 15A breaker.
I have come across some union electricians who run 14 from switches to fixtures but have them on a 20A breaker which IS a problem. I was told that they have been taught this for years because they are using the tap rule. OK, really?
Anyway, the first subject is a bit touchy because it makes it difficult to perform an inspection when all of the wires coming into the panel are 12 but many of the circuits have 14 in them too.
There is nothing against code mixing wire size for these circuits as long as the OCPD matches the smallest wire. We ask them to mark the wires with tags in the panel so that in the future and for final inspection, we know what is what. I wish it was in the code to require marking the maximum OCPD or stating the smallest wire size in the panel ON the wire (probably with non-conductive, not flammable tags). This has been a sore subject and no one has given us a hard time about marking them, even though it is not code and we simply tell them that's what we would like to see now that you have mixed 12 n 14.
Of course commercial is another story due to voltage drop, etc. but I posted this in residential.
I have come across some union electricians who run 14 from switches to fixtures but have them on a 20A breaker which IS a problem. I was told that they have been taught this for years because they are using the tap rule. OK, really?
Anyway, the first subject is a bit touchy because it makes it difficult to perform an inspection when all of the wires coming into the panel are 12 but many of the circuits have 14 in them too.
There is nothing against code mixing wire size for these circuits as long as the OCPD matches the smallest wire. We ask them to mark the wires with tags in the panel so that in the future and for final inspection, we know what is what. I wish it was in the code to require marking the maximum OCPD or stating the smallest wire size in the panel ON the wire (probably with non-conductive, not flammable tags). This has been a sore subject and no one has given us a hard time about marking them, even though it is not code and we simply tell them that's what we would like to see now that you have mixed 12 n 14.
Of course commercial is another story due to voltage drop, etc. but I posted this in residential.