Anyone got a code section....15 amp breaker, 12 ga wire leaves panel, goes in to 4" square in basement, comes out 14ga.....is it a violation? Or not until someone sees the 12 ga. and ups to a 20 amp breaker?
Do you require the labeling for circuits that are up sized for voltage drop?jar546 said:Paul brings up a good point that our company requires. If you mix sizes, we want the circuit labeled with a maximum OCPD size. Nothing but bad can happen when a new owner or electrician changes the breaker size based on the size of the conductor connected to the OCPD.
No sir, we do not but every case is different and we should ask them if there is a decrease in wire size on the other end.raider1 said:Do you require the labeling for circuits that are up sized for voltage drop?Chris