212.12(D) Branch Circuit Extensions or Modifications — Dwelling Units, Dormitory Units, and Guest Rooms and Guest Suites.Where branch circuit wiring for any of the areas specified in210.12(A), (B), or (C) is modified, replaced, or extended, the branch circuit shall be protected by one of the following:
The situation is the following. The existing 200A residential service panel is located on an exterior wall of a garage. There is 30 slimline breakers and the customer wants a service upgrade with a sub-panel in the garage. The existing circuits can be intercepted and land at the sub-panel without adding conductor. The circuits would in fact have less conductor.
Would this require AFCI protection for the circuits in the sub-panel for those circuits that require AFCI in section 210.12(A).
Is this a modification per code. Keep in mind that the new sub-panel seems to not be an issue given that a new main service panel can be installed without AFCI as long as there is no additional conductor length greater than six feet. Again, if a new service panel is not a modification that would trigger AFCI protection does it make sense to decide that the sub-panel is a modification?
210.12(A) Dwelling Units. All 120-volt, single-phase, 15- and 20-ampere branch circuits supplying outlets or devices installed indwelling unit kitchens, family rooms, dining rooms, livingrooms, parlors, libraries, dens, bedrooms, sunrooms, recreation rooms, closets, hallways, laundry areas, or similar rooms or areas shall be protected by any of the means described in 210.12(A) (1) through (6):
The situation is the following. The existing 200A residential service panel is located on an exterior wall of a garage. There is 30 slimline breakers and the customer wants a service upgrade with a sub-panel in the garage. The existing circuits can be intercepted and land at the sub-panel without adding conductor. The circuits would in fact have less conductor.
Would this require AFCI protection for the circuits in the sub-panel for those circuits that require AFCI in section 210.12(A).
Is this a modification per code. Keep in mind that the new sub-panel seems to not be an issue given that a new main service panel can be installed without AFCI as long as there is no additional conductor length greater than six feet. Again, if a new service panel is not a modification that would trigger AFCI protection does it make sense to decide that the sub-panel is a modification?
210.12(A) Dwelling Units. All 120-volt, single-phase, 15- and 20-ampere branch circuits supplying outlets or devices installed indwelling unit kitchens, family rooms, dining rooms, livingrooms, parlors, libraries, dens, bedrooms, sunrooms, recreation rooms, closets, hallways, laundry areas, or similar rooms or areas shall be protected by any of the means described in 210.12(A) (1) through (6):