Can the required outdoor air for a commercial kitchen be supplied by the makeup air unit for the hood? If so, does the makeup air unit need to be sized to meet the requirements of the hood and the outdoor air? (2018 IMC which requires OA for kitchens)
Can the required kitchen exhaust (.7cfm/^ft) be provided by the hood exhaust?
Example: If a hood requires 4400 exhaust cfm, and the kitchen space requires 400 exhaust cfm (based on the .7), then does the hood and the makeup air (from all sources) need to equal (or close) 4800cfm? If the kitchen space requires 200cfm of outdoor air, does the makeup air then need to provide 5000cfm?
Code would require the makeup air to be interlocked with the hood, therefore it would only operate while cooking, likewise the hood would only provide the .7 exhaust when cooking. So in the absence of cooking, if all exhaust and outdoor air were provided by the interlocked cooking system, the kitchen would be left without exhaust and outdoor air.
Sorry, this stuff confuses me a little.
Can the required kitchen exhaust (.7cfm/^ft) be provided by the hood exhaust?
Example: If a hood requires 4400 exhaust cfm, and the kitchen space requires 400 exhaust cfm (based on the .7), then does the hood and the makeup air (from all sources) need to equal (or close) 4800cfm? If the kitchen space requires 200cfm of outdoor air, does the makeup air then need to provide 5000cfm?
Code would require the makeup air to be interlocked with the hood, therefore it would only operate while cooking, likewise the hood would only provide the .7 exhaust when cooking. So in the absence of cooking, if all exhaust and outdoor air were provided by the interlocked cooking system, the kitchen would be left without exhaust and outdoor air.
Sorry, this stuff confuses me a little.