1. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

More Than One Service Disconnect Residential

Discussion in 'Electrical Codes' started by jar546, Jul 13, 2019.

  1. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,215
    Likes Received:
    553
    How many of you see more than one service disconnect for a house? This is normally seen with the use of Automatic Transfer Switches rated as service entrance equipment for use with a generator but his has been used before for larger services on high-end homes with 400 or 600A services.

    Once I get some answers I will continue the reason behind the post.
     
  2. Rick18071

    Rick18071 Sawhorse

    Joined:
    Nov 28, 2009
    Messages:
    2,203
    Likes Received:
    272
  3. Pcinspector1

    Pcinspector1 Platinum Member

    Joined:
    Oct 28, 2009
    Messages:
    3,041
    Likes Received:
    404
    I have seen it done once on an existing single family home converted to a duplex then converted back to a single family.

    The POCO was okay with two exiting meters on the house. I was not so keen with it, but the house would require additional electrical work to by-pass the second meter. The homeowner was okay even after I told him he's going to get two bills with two charges for having the additional service.

    Other than this situation I have not seen two meters on a single family or have any large homes that have required two meters. Out buildings with a separate meter I have seen a numerous times.

    Maybe not the answers your looking for?
     
  4. Paul Sweet

    Paul Sweet Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    1,159
    Likes Received:
    180
    At one time some utilities metered electric water heaters separately.
     
    jar546 likes this.
  5. ICE

    ICE Sawhorse

    Joined:
    Jun 23, 2011
    Messages:
    8,456
    Likes Received:
    919
    They do it now for electric vehicle chargers.
     
  6. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,215
    Likes Received:
    553
    I'm not talking about separate services with separate meters, I am talking about separate disconnects, such as a 320 continuous or 400A or 600A service.
     
  7. Rick18071

    Rick18071 Sawhorse

    Joined:
    Nov 28, 2009
    Messages:
    2,203
    Likes Received:
    272
    2015 IRC E3601.7 Maximum number of disconnects. The service
    disconnecting means shall consist of not more than six
    switches or six circuit breakers mounted in a single enclosure
    or in a group of separate enclosures. [230.71(A)]
     
  8. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    6,673
    Likes Received:
    930
    Never for a house.....Although I inspected a 400A one that they then later service "Tapped" into a grow house....
     