According to the answer man, the 2 hours is right there in Table 601 under Type IIIB construction, Bearing Walls, Exterior: 2
The fact that footnote a excludes the columns, girders, etc carried no weight.
His primary argument was from 714.5, "Load-bearing structural members located within exterior walls or on the outside of a building or structure shall be determined in accordance the highest fire-resistance rating as determined in accordance with the following:
1. Table 601 for the element according to construction type. (Exterior wall, IIIB - 2 hr)
2. Table 601 for exterior bearing walls based upon construction type. (Exterior wall, IIIB - 2 hr)
2. Table 602 for exterior walls based upon fire separation distance (30' clear - 0 hr)
He basically agreed that the "within the exterior wall" part of the definition was a poor choice of words and pointed to the 2000 edition where it was more clearly stated as "Structural members located in exterior walls or along the outer lines of a building or structure shall be protected as required by Table 601 for exterior bearing walls based on the type of construction."
Using that wording, it's hard to say that the steel main frame members at the purlin line of the exterior wall is not included in the requirement to be rated as according to bearing walls, again a 2 hr requirement.
So, brudgers, yes there is a structural frame and because it is along the exterior wall, must be rated as for an exterior bearing wall. Whether bearing or non-bearing and 30' or more separation is not a mitigating factor.
So, mtlogcabin, bearing/non-bearing walls, not a factor. The frame must be rated 2hr because it is structure that is "within" (or more clearly in 2000 IBC, "along the outer lines of the building") the outer wall.
As such, I cannot go with IIIB construction and will go with VB and use a firewall to break it down to legal portions.