midwestFCO
Bronze Member
Sorry so long; trying to be thorough.
I have a lawn mower/small equipment repair facility in our jurisdiction that has changed the way they empty and refill fuel since their 2011 inspection. It just happens that O S H A was out for an inspection (unrelated issue) and came across the new operation before we did their 2012 inspection and contacted us to do the violations of the fire code. The new process involves emptying the oil and/or gasoline (some 2-cycle some 4) into an oil pan then into a 30-gallon drum during the day which is then suctioned into a used (waste) oil tank inside the building - approximately 660 gallon tank. They also sometimes keep a drum (about 30 gallons) in a flammable liquids cabinet if it is not full enough to suction. When the 660-gallon tank is full, they have a company come suction it to dispose.
They then use an air fed refueling dispenser near a self-contained (wood) fueling area, approximately 2'w x 4'l and 8'h. There is no electric to the dispensing unit itself (or the suction unit for the spent fuel) as it is all air-driven. There are electric receptacles in the vicinity, maybe 6 feet or so away. Ceilings in the facility are approximately 15' high. There is no special ventilation around the dispensing/collection areas. Building is unprotected type 2 with full sprinkler system and fire alarm, S-1 use group (for now).
Here is what I have so far:
1 - Tanks need permits. Both tanks are inside and appear to be steel, but no visible UL listing/rating or capacity information. No spill protection or secondary containment. We permit all tanks in our city and they would not be approved as they are now.
2 - The have exceeded their maximum allowable quantity, even with the increases for sprinkler protection and flammable cabinets (they store some used oil in a drum in a cabinet).
3 - They are grounding 55-gallon drums to the sprinkler riser.
4 - Unlisted and likely non-allowed dispensing within the building.
I think they are going to be classified as H use group based on the quantity they have. This will cause them to likely build a special area - maybe exhausted enclosure or maybe an attached addition.
Can anyone think of anything I am missing based on this very basic overview? I am trying to keep their costs down, but I really do not see a way for them to keep the same operation without constructing a room for this purpose. That would be cheaper than making the whole space H2.
Thanks!
I have a lawn mower/small equipment repair facility in our jurisdiction that has changed the way they empty and refill fuel since their 2011 inspection. It just happens that O S H A was out for an inspection (unrelated issue) and came across the new operation before we did their 2012 inspection and contacted us to do the violations of the fire code. The new process involves emptying the oil and/or gasoline (some 2-cycle some 4) into an oil pan then into a 30-gallon drum during the day which is then suctioned into a used (waste) oil tank inside the building - approximately 660 gallon tank. They also sometimes keep a drum (about 30 gallons) in a flammable liquids cabinet if it is not full enough to suction. When the 660-gallon tank is full, they have a company come suction it to dispose.
They then use an air fed refueling dispenser near a self-contained (wood) fueling area, approximately 2'w x 4'l and 8'h. There is no electric to the dispensing unit itself (or the suction unit for the spent fuel) as it is all air-driven. There are electric receptacles in the vicinity, maybe 6 feet or so away. Ceilings in the facility are approximately 15' high. There is no special ventilation around the dispensing/collection areas. Building is unprotected type 2 with full sprinkler system and fire alarm, S-1 use group (for now).
Here is what I have so far:
1 - Tanks need permits. Both tanks are inside and appear to be steel, but no visible UL listing/rating or capacity information. No spill protection or secondary containment. We permit all tanks in our city and they would not be approved as they are now.
2 - The have exceeded their maximum allowable quantity, even with the increases for sprinkler protection and flammable cabinets (they store some used oil in a drum in a cabinet).
3 - They are grounding 55-gallon drums to the sprinkler riser.
4 - Unlisted and likely non-allowed dispensing within the building.
I think they are going to be classified as H use group based on the quantity they have. This will cause them to likely build a special area - maybe exhausted enclosure or maybe an attached addition.
Can anyone think of anything I am missing based on this very basic overview? I am trying to keep their costs down, but I really do not see a way for them to keep the same operation without constructing a room for this purpose. That would be cheaper than making the whole space H2.
Thanks!