I was also a bit surprised that a company that supplies equipment for a 517 environment would publish that detail.manchesterspark said:Chris - I figured 4 days with no responses was good enough to consider this thread was not going to get any more so..............That drawing in the original post is full of errors!
The first one is they show a MC /AC connector but refer to it as a romex connector
The second one is they refer to an aluminum "ground ground wire" to be wrapped around the cable sheath. It IS NOT A GROUND WIRE ! It is a bond wire as the cable is armored cable ( ac cable). As per the manufacture it can be just cut off or wrapped around the cable sheath.
The third one they do not show the box being grounded with the ground inside the ac cable.