I have a client that does multifamily development all over the southeast. We have a project with them that involves several 4-story "breezeway" or open-ended corridors serving the apartments. The construction type is V-A and the project is sprinklered. My reading of code (and that of several other architects I've talked to) is that per V-A, the floor assembly in these breezeways needs to be 1hr rated. The developer is claiming that they've done these in PT wood in multiple states with no issue (and they have...I've seen a few and even have the plans from another architect showing as such), but I don't see a code argument for that being allowed. Am I wrong? Don't want to get on my high horse with the client if there's a loophole (even if I personally don't think there should be). The project is in NC under 2015 IBC. Thanks!