In Virginia it would be an F/S-1 but sprinklers and wood cabinets required.
From the 2009 Virginia Construction Code
Note that R-5 is IRC buildings.
CHAPTER 3
USE AND OCCUPANCY CLASSIFICATION
Change exception 13 of Section 307.1 of the IBC to read:
13. The storage of black powder, smokeless propellant and small arms primers in Groups M, R-3 and R-5 and special
industrial explosive devices in Groups B, F, M and S, provided such storage conforms to the quantity limits and
requirements prescribed in the International Fire Code, as amended in Section 307.9.
Add Section 307.9 to the IBC to read:
307.9 Amendments. The following changes shall be made to the International Fire Code for the use of Exception 13 in
Section 307.1:
1. Change Section 314.1 of the IFC to read as follows:
314.1 General. Indoor displays constructed within any building or structure shall comply with Sections 314.2
through 314.5.
2. Add new Section 314.5 to the IFC to read as follows:
314.5 Smokeless powder and small arms primers. Vendors shall not store, display or sell smokeless powder
or small arms primers during trade shows inside exhibition halls except as follows:
1. The amount of smokeless powder each vender may store is limited to the storage arrangements and
storage amounts established in Section 3306.5.2.1.
2. Smokeless powder shall remain in the manufacturer’s original sealed container and the container
shall remain sealed while inside the building. The repackaging of smokeless powder shall not be
performed inside the building. Damaged containers shall not be repackaged inside the building and
shall be immediately removed from the building in such manner to avoid spilling any powder.
3. There shall be at least 50 feet separation between vendors and 20 feet from any exit.
4. Small arms primers shall be displayed and stored in the manufacturer’s original packaging and in
accordance with the requirements of Section 3306.5.2.3.
3. Change Exception 4 and add Exceptions 10 and 11 to Section 3301.1 of the IFC as follows:
4. The possession, storage and use of not more than 15 pounds (6.75 kg) of commercially manufactured
sporting black powder, 20 pounds (9 kg) of smokeless powder and any amount of small arms primers for
hand loading of small arms ammunition for personal consumption.
10. The display of small arms primers in Group M when in the original manufacturer’s packaging.
11. The possession, storage and use of not more than 50 pounds (23 kg) of commercially manufactured
sporting black powder, 100 pounds (45 kg) of smokeless powder, and small arms primers for hand
loading of small arms ammunition for personal consumption in Group R-3 or R-5, or 200 pounds (91 kg)
of smokeless powder when stored in the manufacturer’s original containers in detached Group U
structures at least 10 feet (3048 mm) from inhabited buildings and are accessory to Group R-3 or R-5.
4. Change the definition of Smokeless Propellants in Section 3302.1 of the IFC as follows:
SMOKELESS PROPELLANTS. Solid propellants, commonly referred to as smokeless powders, or any
propellants classified by DOTn as smokeless propellants in accordance with NA3178 (Smokeless Powder for
Small Arms), used in small arms ammunition, firearms, cannons, rockets, propellant-actuated devices and
similar articles.
5. Change Section 3306.4 of the IFC to read as follows:
3306.4 Storage in residences. Propellants for personal use in quantities not exceeding 50 pounds (23 kg) of
black powder or 100 pounds (45 kg) of smokeless powder shall be stored in original containers in occupancies
limited to Group R-3 and R-5 or 200 pounds (91 kg) of smokeless powder when stored in the manufacturer’s
original containers in detached Group U structures at least 10 feet (3048 mm) from inhabited buildings and
are accessory to Group R-3 or R-5. In other than Group R-3 or R-5, smokeless powder in quantities exceeding
20 pounds (9 kg) but not exceeding 50 pounds (23 kg) shall be kept in a wooden box or cabinet having walls
of at least one inch (25 mm) nominal thickness or equivalent.
6. Delete Sections 3306.4.1 and 3306.4.2 of the IFC.
7. Change Section 3306.5.1.1 of the IFC to read as follows:
3306.5.1.1 Smokeless propellant. No more than 100 pounds (45 kg) of smokeless propellants in containers of
eight pounds (3.6 kg) or less capacity shall be displayed in Group M occupancies.
8. Delete Section 3306.5.1.3 of the IFC.
9. Change Section 3306.5.2.1 of the IFC as follows:
3306.5.2.1 Smokeless propellant. Commercial stocks of smokeless propellants shall be stored as follows:
1. Quantities exceeding 20 pounds (9 kg), but not exceeding 100 pounds (45 kg) shall be stored in
portable wooden boxes having walls of at least one inch (25 mm) nominal thickness or equivalent.
2. Quantities exceeding 100 pounds (45 kg), but not exceeding 800 pounds (363 kg), shall be stored in
storage cabinets having walls at least one inch (25 mm) nominal thickness or equivalent. Not more
than 400 pounds (182 kg) shall be stored in any one cabinet, and cabinets shall be separated by a
distance of at least 25 feet (7620 mm) or by a fire partition having a fire-resistance rating of at least
one hour.
3. Storage of quantities exceeding 800 pounds (363 kg), but not exceeding 5,000 pounds (2270 kg) in a
building shall comply with all of the following:
3.1. The storage is inaccessible to unauthorized personnel.
3.2. Smokeless propellant shall be stored in nonportable storage cabinets having wood walls at least
one inch (25 mm) nominal thickness or equivalent and having shelves with no more than 3 feet
(914 mm) of vertical separation between shelves.
3.3. No more than 400 pounds (182 kg) is stored in any one cabinet.
3.4. Cabinets shall be located against walls with at least 40 feet (12 192 mm) between cabinets. The
minimum required separation between cabinets may be reduced to 20 feet (6096 mm) provided
that barricades twice the height of the cabinets are attached to the wall, midway between each
cabinet. The barricades must extend a minimum of 10 feet (3048 mm) outward, be firmly
attached to the wall, and be constructed of steel not less than 0.25 inch thick (6.4 mm), 2-inch
(51 mm) nominal thickness wood, brick, or concrete block.
3.5. Smokeless propellant shall be separated from materials classified as combustible liquids,
flammable liquids, flammable solids, or oxidizing materials by a distance of 25 feet (7620 mm)
or by a fire partition having a fire-resistance rating of 1 hour.
3.6. The building shall be equipped throughout with an automatic sprinkler system installed in
accordance with Section 903.3.1.1.
4. Smokeless propellants not stored according to Item 1, 2, or 3 above shall be stored in a Type 2 or 4 magazine
in accordance with Section 3304 and NFPA 495.