• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

NEC 250.50 Separate Building

Does the fact that this is going to be a separate building receiving power from the service of another building? Does the fact that there will be a feeder serving this building with grounds and neutrals separated?
Those are immaterial. There is no requirement in the NEC to identify a Grounding Electrode Conductor with the color green. Conversely there is no prohibition.

Cheers, Wayne
 
Yep...discussed this at my last monthly get together...EGC needs to be identified...Not GEC...Bunch of electricians did not know that...
 