NEC 250.8(A)(6) Connection of Grounding & Bonding Equipment

jar546

CBO
Joined
Oct 16, 2009
Messages
12,996
Location
Not where I really want to be
This is becoming all too common a violation. Tapcon screws into the masonry behind the box to ground a box, in violation of NFPA 70 Section 250.8(A)(6). How often do you see this or something similar?

This should have been a thread forming screw engaged into the metal of the panel itself by at least 2 threads such as a 10-32 screw.

IMG_6844.JPG
 
I have never allowed a random screw as the sole connection to an enclosure unless that screw was provided at that location for that purpose. The sheet metal is not thick enough to achieve two threads. This guy tried to beat me at my own game. One thread.... two screws.

49112250593_a22e49823b_b.jpg
 
Last edited:
They got some threads on this one. Couldn't be any more wrong but their heart is in the right place.

49112324443_8429efd082_b.jpg

49112833201_6dbfd2b14a_b.jpg
 
Last edited:
This is becoming all too common a violation. Tapcon screws into the masonry behind the box to ground a box, in violation of NFPA 70 Section 250.8(A)(6). How often do you see this or something similar?

This should have been a thread forming screw engaged into the metal of the panel itself by at least 2 threads such as a 10-32 screw.

View attachment 6152
shouldn't 250.126 also apply
 