• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

NEC 310.12(A) One-Family Dwelling Service Conductors & Feeders

Why then is the 100% factor mentioned in 310.12(B) with regards to a dwelling feeder? In what circumstance would the 100% of the load apply to a dwelling feeder?
Any multifamily building (even a duplex) will likely have a service that supplies multiple dwelling units, and that service does not meet the requirements of 310.12(A). But then if a dwelling unit has a subpanel in it that supplies all the dwelling unit's loads, the feeder to that subpanel would satisfy 310.12(B), assuming it is rated between 100A and 400A.

Cheers, Wayne
 
  • Like
Reactions: ICE
This was a problem for 100A exterior main disco "services" here where they would put the main outside and run what they normally would for a service sized SER in and then they would have to put a smaller main breaker in as the feeder and service ampacities were/ are different....
 