Section 445.18 of the 2020 NEC lays out some pretty clear but layered requirements for generator disconnecting means and emergency shutdown. A few key takeaways:
  • All generators (other than cord-and-plug portable types) require a disconnecting means that opens all ungrounded conductors and can be locked open [445.18(A)].
  • Provisions must be in place to shut down the prime mover and disable start circuits [445.18(B)].
  • For units above 15 kW, a remote emergency stop switch is required outside the room or enclosure [445.18(C)].
  • One- and two-family dwellings now require an exterior emergency shutdown device [445.18(D)].
  • For parallel installations, isolation of generator output terminals is required [445.18(E)].
The enhanced content even notes that the emergency engine shutdown can double as the disconnecting means, but only if it can be locked in the open position.

In practice, how are you seeing these requirements enforced in the field—especially the remote emergency shutdown requirement for generators above 15 kW and the exterior emergency shutdown for one- and two-family dwellings? Are AHJs requiring strict compliance on retrofit installations, or are you seeing flexibility depending on the type of occupancy and system?
 