• Welcome to The Building Code Forum

    Your premier resource for building code knowledge.

    This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.

    Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.

    Ready to upgrade? Log in and upgrade now.

NEC 517.80: Communications and Low-Voltage Systems in Patient Care Spaces

jar546

CBO
Joined
Oct 16, 2009
Messages
12,816
Location
Not where I really want to be

What is NEC 517.80 About?​

NEC 517.80 deals with the requirements for certain types of low-voltage electrical systems used in patient care spaces. These systems include:
  • Communications systems
  • Signaling systems
  • Data systems
  • Fire alarm systems
  • Systems operating at less than 120 volts
The key point is ensuring that these systems have similar levels of insulation and isolation as the main electrical systems in patient care areas. This is crucial to protect patients from potential electrical hazards.

Why is Insulation and Isolation Important?​

In patient care areas, patients might be more vulnerable to electrical shocks due to their medical conditions or the procedures they are undergoing. Proper insulation and isolation prevent any accidental contact with electrical circuits, thus minimizing the risk of electrical shock.

Key Requirements of 517.80​

  1. Insulation and Isolation:
    • The low-voltage systems (communications, signaling, data, fire alarm) must have insulation and isolation equivalent to that of the main electrical systems in patient care areas.
  2. Exemptions for Certain Circuits:
    • Class 2 and Class 3 Signaling and Communications Systems:
      • These systems do not need to meet the grounding and mechanical protection requirements specified in 517.13 and 517.31(C)(3)(5).
      • They do not need to be enclosed in raceways unless required by Chapters 7 or 8 of the NEC.
    • Class 2 Circuits Transmitting Power and Data:
      • These circuits are also exempt from the same grounding and mechanical protection requirements.
    • Power-Limited Fire Alarm Systems:
      • Similar exemptions apply unless specified otherwise by the relevant chapters.
  3. Transformer-Powered Secondary Circuits:
    • These circuits, used for communications or signaling systems, also do not need to be enclosed in raceways unless specified by Chapters 7 or 8.

Informational Note​

  • ANSI/NEMA C137.3-2017:
    • This standard provides guidance on the installation of energy-efficient Power over Ethernet (PoE) lighting systems, highlighting the importance of proper installation techniques for these low-voltage systems.

Main Objective​

The primary goal of these requirements is to minimize the risk of electrical shock to patients by ensuring that even low-voltage systems are adequately insulated and isolated. This is especially important in environments where patients are undergoing medical treatment and might be more sensitive to electrical hazards.

Practical Example for Inspectors​

  • Nurse Call Systems, Intercoms, and Fire Alarms:
    • These systems fall under the specified categories. For example, a nurse call system in a hospital room needs to have proper insulation to prevent any accidental electrical contact.
    • The system might use Class 2 circuits, which are designed to operate at low voltage and power levels, making them inherently safer. However, the insulation and isolation requirements ensure an additional layer of safety.

Summary for Electrical Inspectors​

  • Ensure that communications, signaling, data, and fire alarm systems in patient care spaces have equivalent insulation and isolation as the main electrical systems.
  • Remember the exemptions for Class 2 and Class 3 systems regarding grounding and mechanical protection.
  • Verify compliance with Chapters 7 or 8 for specific installation requirements, like using raceways.
  • Keep patient safety as the top priority by minimizing exposure to electrical hazards.
 
Back
Top