• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Need NFPA 13?

Corridor is defined in Chapter 2 as "An enclosed exit access component that defines and provides a path of egress travel" An exterior balcony isn't enclosed, so I don't think this would apply.

If it does apply, could the private balcony be extended to the end of the stair, or could the stair direction be reversed to reduce the distance to 20 ft.?
 
This might be the issue....

1021.1 General. Balconies used for egress purposes shall
conform to the same requirements as corridors for minimum
width, required capacity, headroom, dead ends and projections.

But extending the private balcony on the left does seem like an easy solution....
 
yeah, 1021.1 seems like a 'gotcha'.

But extending the private balcony on the left does seem like an easy solution....

that would work for the 3rd floor, but not the 2nd floor, it seems, as i need an egress bath (magenta) through there.

1653677951775.png


If it does apply, could the private balcony be extended to the end of the stair, or could the stair direction be reversed to reduce the distance to 20 ft.?

too late for flipping. :)
 