No there are no NEC tables that provide the area of NM cable. Each manufacture may have a different thickness of outer sheath etc. You need to get the information from the manufacture.Pcinspector1 said:codeworks,Field inspection with three romex in 3/4" EMT in basement for switches next to foundation, protection to the top of the wall as gfretwell pointed out, above FF.
gfretwell,
So theres no table for ROMEX type wiring which accounts for the jacket, you have to know the wire manufacture? Is southwire only in metric?
pc1
See Note 2 in Chapter Nine for the information you are seekingPcinspector1 said:codeworks,Field inspection with three romex in 3/4" EMT in basement for switches next to foundation, protection to the top of the wall as gfretwell pointed out, above FF.