Adopted city fire code is 2006 IFC
College owned building, 2 stories from ground level with basement that has ground level exit discharge in the back. The building has a large assembly area 800 capacity, the rest is office space. No classrooms, no residential in the structure. Building is over 30 years old, not protected, last remodel was in 1998 and no changes were made to the fire alarm that we know of. They are wanting now to replace existing alarm system completely.
Community Development director says he can't see where it would be required to bring the new fire alarm system up to current code standards. What I can't find is where it says in the code that the new alarm in the existing occupancy has to be to current code. It just seems like common sense to me that a total replacement would constitute a new system and therefore fall under the criteria for a new install.
Other question is; are smoke detectors required in the large assembly area (800 capacity)? They were wanting to know if duct detectors would suffice in place of open air detectors. I have the answer to that (NFPA 72 5.14.2a) - no. I just can't find where it is required for open air smoke detectors in the large assembly area. For that matter where are they required in this occupancy?
College owned building, 2 stories from ground level with basement that has ground level exit discharge in the back. The building has a large assembly area 800 capacity, the rest is office space. No classrooms, no residential in the structure. Building is over 30 years old, not protected, last remodel was in 1998 and no changes were made to the fire alarm that we know of. They are wanting now to replace existing alarm system completely.
Community Development director says he can't see where it would be required to bring the new fire alarm system up to current code standards. What I can't find is where it says in the code that the new alarm in the existing occupancy has to be to current code. It just seems like common sense to me that a total replacement would constitute a new system and therefore fall under the criteria for a new install.
Other question is; are smoke detectors required in the large assembly area (800 capacity)? They were wanting to know if duct detectors would suffice in place of open air detectors. I have the answer to that (NFPA 72 5.14.2a) - no. I just can't find where it is required for open air smoke detectors in the large assembly area. For that matter where are they required in this occupancy?