3 story apartment Type V-B building. Each dwelling unit has a gas fireplace installed within a concealed space. typical installation with the vent exhausting out the top of the unit within the concealed space and entering a rated shaft at the floor ceiling assembly. Would you require a sprinkler head above this fireplace?
6.6.6
Sprinklers shall not be required in attics, penthouse equipment rooms, elevator machine rooms, concealed spaces dedicated exclusively to and containing only dwelling unit ventilation equipment, crawl spaces, floor/ceiling spaces......
6.6.6.1
When fuel fired equipment is present. at least one quick-response intermediate temperature sprinkler shall be installed above the equipment.