2018 IBC. I have a proposed R2, 3 stories, VB. Proposing a 13R. The floor plate is 21,864sf². The allowable area per t506.2 is 7,000sf² when a 13R is used. The DP is claiming they can use the 13R system allowable area because 903.3.1.2 says a 13R system can be installed. They do take a frontage increase, but it is not relevant to the issue I see. Do I completely misunderstand t506.2 & 903.3.1.2?