Insurance Engineer
The complete draft report is available online at http://www.nist.gov/el.
Part 1
CHARLESTON, S.C.—Major factors contributing to a rapid spread of fire at the Sofa Super Store in Charleston, S.C., on June 18, 2007, included large open spaces with furniture providing high fuel loads, the inward rush of air following the breaking of windows and a lack of sprinklers, according to a draft report released for public comment today by the U.S. Commerce Department's National Institute of Standards and Technology (NIST). The fire trapped and killed nine firefighters, the highest number of firefighter fatalities in a single event since 9/11.
Based on its findings, the NIST technical study team made 11 recommendations for enhancing building, occupant and firefighter safety nationwide. In particular, the team urged state and local communities to adopt and strictly adhere to current national model building and fire safety codes.1 If today’s model codes had been in place and rigorously followed in Charleston in 2007, the study authors said, the conditions that led to the rapid fire spread in the Sofa Super Store probably would have been prevented.
“Furniture stores typically have large amounts of combustible material and represent a significant fire hazard,” said NIST study leader Nelson Bryner. “Model building codes should require both new and existing furniture stores to have automatic sprinklers, especially if those stores include large, open display areas.”
Specifically, the NIST report calls for national model building and fire codes to require sprinklers for all new commercial retail furniture stores regardless of size, and for existing retail furniture stores with any single display area of greater than 190 square meters (2,000 square feet). Other recommendations include adopting model codes that cover high fuel load situations (such as a furniture store), ensuring proper fire inspections and building plan examinations, and encouraging research for a better understanding of fire situations such as venting of smoke from burning buildings and the spread of fire on furniture.
Using a state-of-the-art computer model to simulate the fire, the study team found that the addition of automatic sprinklers inside the loading dock could have significantly slowed the fire (which began just outside the dock area), prevented it from spreading beyond the dock, and eventually, extinguished it completely. The model also showed that sprinklers on the loading dock likely would have maintained what firefighters call tenability conditions, the ability for individuals in a fire event to escape unassisted.
Factors identified as contributing to the fire’s progress include: (1) the high fuel loads—especially furniture—present throughout the building; (2) the lack of sprinklers throughout the Sofa Super Store; (3) the open floor plan of the facility; (4) the hidden build-up of combustible smoke and gases in the area between the drop ceiling and the roof of the main showroom; (5) the non-fire-activated roll-up door that was open between the loading dock and the holding area; (6) the four fire-activated roll-up doors (out of seven) that activated but did not close during the fire; (7) the metal walls in the warehouse and west showroom that allowed heat from the fire to ignite items next to the walls; and (8) the breaking of windows at the front of the store that supplied air to the fire.
NIST’s team of experts traveled to Charleston to gather data within 36 hours of the Sofa Super Store fire. Using these data and other information collected in the following months (such as building design documents, records, plans, video and photographic data, radio transmissions, interviews with emergency responders, and informal discussions with store employees), the NIST study team developed its computer model to simulate and analyze the characteristics of the fire, including fire spread, smoke movement, tenability, and the operation of active and passive fire protection systems.
Based on their model and the data collected, the NIST researchers determined the following sequence of events on June 18, 2007, at the Sofa Super Store:
•The fire began in trash outside the loading dock and spread into the enclosed loading dock. The fire spread from the exterior to the interior of the loading dock, which was used for staging furniture for delivery and repair. The fire spread quickly within the loading dock and moved into both the retail showroom and warehouse spaces.
•During the early stages of this fire, the fire was unable to access enough air, a state that slowed its growth. However, the lack of sufficient air for complete combustion did result in large volumes of smoke and combustible gases flowing into the space below the roof and above the drop ceiling of the main retail showroom.
•The fire spread to the rear of the main showroom through the holding area and ignited additional fuel in the rear of the main showroom, at which time it became more visible to firefighters in the main showroom.
•The growth of the fire at the back of the main showroom was still slowed by the lack of air. As the fire burned in the rear of the main showroom, the fire pumped more hot unburned fuel into the smoke layer below the drop ceiling. The lack of air prevented the unburned fuel in the smoke layer from igniting.
•When the front windows were broken (approximately 24 minutes after firefighters arrived at the store), additional air flowed in the front windows, along the floor and to the rear of the showroom, and became available to the fire. The additional air allowed the burning rate of the fire to increase rapidly and ignite the layer of unburned fuel below the drop ceiling.
•The fire swept from the rear to the front of the main showroom extremely quickly, then into the west and east showrooms, trapping six firefighters in the main showroom and three firefighters in the west showroom.
•Furniture and merchandise in the showrooms and warehouse continued to burn for an additional 140 minutes before the fire was extinguished.
Part 1