NM cable clamps

I don't see an issue with it as straps don't have to be listed and the cable is supported and strapped. The title says cable clamps so I am confused but I am assuming you mean strapping.
 
Dennis said:
I don't see an issue with it as straps don't have to be listed and the cable is supported and strapped. The title says cable clamps so I am confused but I am assuming you mean strapping.
We normally see clamps or straps so it's only a play on words.

I will tell everyone that I approved this installation and would again. I love the word "​approved"
 
jar546 said:
Would you approve this, yes or no and why or why not?View attachment 1717
Violation

334.30 Securing and Supporting.

Nonmetallic-sheathed cable shall be supported and secured by staples, cable ties, straps, hangers, or similar fittings designed and installed so as not to damage the cable, at intervals not exceeding 1.4 m (4½ ft) and within 300 mm (12 in.) of every outlet box, junction box, cabinet, or fitting. Flat cables shall not be stapled on edge.

Sections of cable protected from physical damage by raceway shall not be required to be secured within the raceway.
 