jar546
CBO
Very interesting and I hope that you continue to participate in the forum. I hope this is not a hit and run post a link to endorse a product post.booneglyn said:I am an Engineer with the Trus Joist division of Weyerhaeuser. Regarding "Membrane Protection" of light-weight framing (this would include I-joists, plated trusses, and light weight steel joists), these provisions for single-family structures are listed in section R501.3 of the 2012 IRC. As noted earlier, Pennsylvania adopted nearly identical language in their own code.Flak Jacket is a Factory Applied protective coating offered by Trus Joist on our TJI joist products. It's available in the markets where this code provision has been adopted.
No Burn is a Field Applied intumescent paint that can be applied to framing members after installation. While some builders may have used this on TJI joists, Weyerhaeuser does not endorse this product.
We have tested and gained approval of the Flak Jacket coating by meeting the requirements of Exception 4 of R501.3. We have followed the ICC-ES AC-14 Acceptance Criteria which requires a loaded assembly fire test using the E119 time-temperature curves. This assembly test has demonstrated that a floor system built with TJI joists with Flak Jacket protection provides equivalent fire endurance to a floor system built with unprotected 2x10 dimension lumber.
Per our evaluation report, web holes that are within the limits of our standard published hole charts are acceptable without further field treatment.
For more information or questions, you can contact our technical support team from our website Weyerhaeuser :: Flak Jacket Fire Protection.
Is Weyerhauser interested in supporting this forum?