We propose using a UL-listed ventless Convotherm combi oven instead of a traditional Type I hood.
The unit includes an integral filtration system that limits grease-laden vapor emissions.
Testing documentation shows it produces only 1.01 mg/m³ of grease-laden effluents, which meets the code requirement of 5 mg/m³ or less per Section 507.2.
...
Per Section 507.3, the induction range’s heat and moisture loads will be incorporated into the overall HVAC system design.
The range will be used for low-grease cooking methods—soups, sauces, grains, gentle vegetable sautés, and warming/finishing tasks.
There will be no bacon, frying, searing, or other high-temperature cooking.
...
A low-temperature dishwasher will be used, and the HVAC system will accommodate its heat and moisture loads in accordance with Section 507.3 as well.
...
Since the space is a sprinklered A-2 occupancy and no Type I hood is being used, we interpret IBC Table 803.11 to permit Class C FRP wall panels behind the oven and range.
...
Would you agree with the above interpretations?
The unit includes an integral filtration system that limits grease-laden vapor emissions.
Testing documentation shows it produces only 1.01 mg/m³ of grease-laden effluents, which meets the code requirement of 5 mg/m³ or less per Section 507.2.
...
Per Section 507.3, the induction range’s heat and moisture loads will be incorporated into the overall HVAC system design.
The range will be used for low-grease cooking methods—soups, sauces, grains, gentle vegetable sautés, and warming/finishing tasks.
There will be no bacon, frying, searing, or other high-temperature cooking.
...
A low-temperature dishwasher will be used, and the HVAC system will accommodate its heat and moisture loads in accordance with Section 507.3 as well.
...
Since the space is a sprinklered A-2 occupancy and no Type I hood is being used, we interpret IBC Table 803.11 to permit Class C FRP wall panels behind the oven and range.
...
Would you agree with the above interpretations?