Inserting a new duct connecting three stories in an existing Type III-B building (wood floor joists). The floor/ceilings do not not need to be rated. 2018 IBC 716.6.3 says that this duct needs to be protected by a shaft enclosure complying with Section 713. 713.2 says this needs to be a fire barrier as per 707, and 707.5.1 says that supporting construction for a fire barrier needs to be rated, as well.
So, to confirm, does this mean that even though the floor is not required to be rated, I do need to also rate the portions of the floor supporting the shaft enclosure? It's not explicitly stated so and the commentaries often offer a good reminder in situations like this so I'm wondering if the requirement for rating that portion of the floor is not required.
Thoughts?
So, to confirm, does this mean that even though the floor is not required to be rated, I do need to also rate the portions of the floor supporting the shaft enclosure? It's not explicitly stated so and the commentaries often offer a good reminder in situations like this so I'm wondering if the requirement for rating that portion of the floor is not required.