Hello all and thank you for this website. This is my first post and I am hoping to get some help.
Building a hotel VA construction, 4 stories sprinklered. Bearing walls are to be 1HR rating. 1st floor to have all the hotel amenities when you enter (assembly), and then from the lobby there will be a corridor leading to first floor rooms and elevators to go up to other floors. That part of the first floor and upper floors will be Residential R1.
Residential use are to be 0.5 hr with 20 min rating per IBC 708.3 exception 1.
Assembly space corridors do not need to be rated per 1020.1
We have designed the building to most restrictive use A2.
I do not think that i need to separate the Residential area with a fire rated door and panic hardware from the A2 space in the first floor, however i have other people thinking otherwise. Do you guys have any thoughts to the matter?
Building a hotel VA construction, 4 stories sprinklered. Bearing walls are to be 1HR rating. 1st floor to have all the hotel amenities when you enter (assembly), and then from the lobby there will be a corridor leading to first floor rooms and elevators to go up to other floors. That part of the first floor and upper floors will be Residential R1.
Residential use are to be 0.5 hr with 20 min rating per IBC 708.3 exception 1.
Assembly space corridors do not need to be rated per 1020.1
We have designed the building to most restrictive use A2.