Type V-1 hour apartment building, 2021 IBC / 2022 CBC
Exterior walls 13' from property line.
Roof trusses have 1 hour rated roof-ceiling assembly throughout. It qualifies for IBC 705.11 exception#4 which says parapets need not be provided.
Parapets are not being used to provide a fire separation - - they exist to help direct rainwater towards the drains.
QUESTION: when non-required parapets are provided anyway(usually for drainage or for hiding rooftop equipment), do the parapets need to be 1 hour rated, simply because they are in line with the exterior walls of the building below? Do you consider the parapet part of an "exterior wall" if it's not really enclosing space above the roof level?
Proposed nonrated parapet construction, from outside face of wall:
Exterior walls 13' from property line.
Roof trusses have 1 hour rated roof-ceiling assembly throughout. It qualifies for IBC 705.11 exception#4 which says parapets need not be provided.
Parapets are not being used to provide a fire separation - - they exist to help direct rainwater towards the drains.
QUESTION: when non-required parapets are provided anyway(usually for drainage or for hiding rooftop equipment), do the parapets need to be 1 hour rated, simply because they are in line with the exterior walls of the building below? Do you consider the parapet part of an "exterior wall" if it's not really enclosing space above the roof level?
Proposed nonrated parapet construction, from outside face of wall:
- 7/8" stucco
- 1/2" plywood sheathing
- 2x4 studs
- 1/2" plywood sheathing
- TPO roofing, rolled up onto plywood sheathing