Objectionable Current

jar546

CBO
Joined
Oct 16, 2009
Messages
12,994
Location
Not where I really want to be
What code citation would be the best option if you found a sub-panel inside the same building as the origin of the feeder and in that sub-panel, the neutrals and grounds were not separated?

NEC 250.6
NEC 250.142(B)

Or would you cite something else?
 
250.24(A)(5) Load-Side Grounding Connections. A grounded conductor shall not be connected to normally non–current-carrying metal parts of equipment, to equipment grounding conductor(s), or be reconnected to ground on the load side of the service disconnecting means except as otherwise permitted in this article.

Cheers, Wayne
 