A church is currently located in 2 tenant spaces in a Type III-N building constructed in 1997 at an industrial park in California. It was previously approved as an A-3 occupancy
They now want to expand into 4 adjacent spaces (total 9600 SF), changing those spaces from their original F-2 occupancy to A3 occupancy. The existing building and all existing uses in the building are unsprinklered.
Table 505.2 indicates the new A-3 use will need to be sprinklered, just to achieve allowable area. Question that I'm sure my church client will ask: In your opinion, does this mean the entire building needs to be sprinklered? There is a concrete party wall separating the proposed A-3 use from the remaining F-2 use in the building.
They now want to expand into 4 adjacent spaces (total 9600 SF), changing those spaces from their original F-2 occupancy to A3 occupancy. The existing building and all existing uses in the building are unsprinklered.
Table 505.2 indicates the new A-3 use will need to be sprinklered, just to achieve allowable area. Question that I'm sure my church client will ask: In your opinion, does this mean the entire building needs to be sprinklered? There is a concrete party wall separating the proposed A-3 use from the remaining F-2 use in the building.