elinamanvel
REGISTERED
Hi guys!
I need some help with calculating the occupant load.
Here is a spa project 1995 sq and it has big outdoor courtyard 1236 sq. As I understood, I need to use type B for the cosmetic spa salon, but I'm so confused about what areas I should include in the calculations.
According to Table 1004.5 (California building code), for B type, I need to use 150 gross. So gross area is 1995-95 sq ft (interior walls)= 1900. 1900/150=12.6=13 occupant.
If I need to merge the outdoor area and spa area as it has been said in 1004.7 (outdoor areas), then I will get 1900(spa)+1236(courtyard)=3136 sq ft. 3136/150=21 occupant.
And the third way to calculate it is to divide the floor plan into several zones (patient rooms-business(150), reception#1-assembly-standing space(5), reception #1-fixed sitting area(18” linear length; 3 seats), storage-Accessory storage areas, mechanical equipment room (300) and reception#2- assembly without fixed seats-Unconcentrated(7). So, in this case, when I calculated all these small areas as different occupancy types, I am getting 60 occupants, which is not realistic number for this spa. And I also didn't include a courtyard area here.
Please see here ( https://drive.google.com/file/d/1bVCSJTlzmhe6Q49HxlDT9fqB78lFeHH4/view?usp=drivesdk ) the floor plan in the attachment, and let me know your thoughts. Thanks.
I need some help with calculating the occupant load.
Here is a spa project 1995 sq and it has big outdoor courtyard 1236 sq. As I understood, I need to use type B for the cosmetic spa salon, but I'm so confused about what areas I should include in the calculations.
According to Table 1004.5 (California building code), for B type, I need to use 150 gross. So gross area is 1995-95 sq ft (interior walls)= 1900. 1900/150=12.6=13 occupant.
If I need to merge the outdoor area and spa area as it has been said in 1004.7 (outdoor areas), then I will get 1900(spa)+1236(courtyard)=3136 sq ft. 3136/150=21 occupant.
And the third way to calculate it is to divide the floor plan into several zones (patient rooms-business(150), reception#1-assembly-standing space(5), reception #1-fixed sitting area(18” linear length; 3 seats), storage-Accessory storage areas, mechanical equipment room (300) and reception#2- assembly without fixed seats-Unconcentrated(7). So, in this case, when I calculated all these small areas as different occupancy types, I am getting 60 occupants, which is not realistic number for this spa. And I also didn't include a courtyard area here.
Please see here ( https://drive.google.com/file/d/1bVCSJTlzmhe6Q49HxlDT9fqB78lFeHH4/view?usp=drivesdk ) the floor plan in the attachment, and let me know your thoughts. Thanks.