Mark, hence 1/5 sf.Darren Emery said:between services.
When you accept something less than 1/5 sf, how do you prohibit back to back services...or transfer of the property to people with different worship practices or just hiring a different minsiter?Papio Bldg Dept said:We review each on a case by case basis and rely heavily on the RDP to assign the specific use/function of church foyer spaces per their design. Chapter 10 does not assign an occupant load based upon occupancy classification. Churches are not all the same, and their occupant loads are not necessarily easy to assign, especially in foyers. In my experience most catholic and apolostic congregations (circulation only) use their foyer spaces much differently than evangelical and ecumenical congregations (assembly/gatherings/social areas). Some even use their spaces for 48 hour lock-ins, which involve sleeping and could potentially lead to other code requirements. If the RDP wants to assign a 1/5sf occupant load to that area, we will gladly accept it, as this is the most restrictive. On the other hand, if they want to show these areas as a different use/function, with a lower occupant load per square footage, they need to provide us with sufficient documentation to satisfy the reduced occupant load option in Chapter 10(e.g. letter of operations signed by owner/operator).
So with that in mind, all projects should be designed as an H occupancy, just in case......brudgers said:...or transfer of the property
Change of use might trigger a new CO. On the other hand, changes to a congregation would probably not.mark handler said:So with that in mind, all projects should be designed as an H occupancy, just in case......
Without fixed seating, the aisles are considered occupied. If they provide pews in the foyer, they can use them for the occupant load.Architect1281 said:"ZERO" - Non Simultaneous occupancy - does anyone understand the meaning of "NET" "OCCUPIED AREA" so what would the occupant load of the aisles be = ZERO same thing for the restrooms while building is occupied = ZERO Every seat has an A** that is the NET OCCUPANT LOAD - IF the exits can support additional occupants on everybody shows up Easter / Christmas / BINGO then at the owners choice they could declare an increaed occupant load Just my opinion based on definition
A change of use that increases an occupant load, or becomes a more restrictive occupancy will always trigger a new CO because it is a change of occupancy (either type or load)...if we are aware of it.brudgers said:Change of use might trigger a new CO. On the other hand, changes to a congregation would probably not.
see one above standing at 5???mark handler said:Overkill, and not required per code
SO after the service how many are still in the Sanctuary????????Darren Emery said:Agreed. We are currently expanding our facility - specifically to gain more foyer space. It gets absolutely packed in there between services. And not just for a few minutes - no one wants to leave (great problem to have!)
Sooo... a reasonable approach might be to make sure there is exiting for 5 sq ft per in the foyer...but maybe not add that load to the total...some number less than that for total as to make everyone comfortable....it can get abused certainly (I have seen it) post the load, and it becomes a FM enforcement issue....unfortunately....Architect1281 said:SO after the service how many are still in the Sanctuary???????? The building Occupant Load does not need to count me multiple times - I'd like them to it makes me feel more impotent. (sp)![]()
Yep, you count the load of the worship space once and then add it to the standing room capacity of the foyer once.Architect1281 said:SO after the service how many are still in the Sanctuary???????? The building Occupant Load does not need to count me multiple times - I'd like them to it makes me feel more impotent. (sp)![]()
On what code basis do you ignore simultaneous occupancy?steveray said:Sooo... a reasonable approach might be to make sure there is exiting for 5 sq ft per in the foyer...but maybe not add that load to the total...some number less than that for total as to make everyone comfortable....it can get abused certainly (I have seen it) post the load, and it becomes a FM enforcement issue....unfortunately....
Never said I would.....but if someone wants to or thinks it reasonable.....it does not necessarily have to be all or nothing....brudgers said:On what code basis do you ignore simultaneous occupancy?
I don't know that I would say that it is all that amazing... While Table 1004.1.1 does not have a function of space listing for foyers or corridors, in effect, it is silent on those spaces, yet you persist to assign a logical and reasonable assumption that these spaces may also function as assembly spaces in an overflow situation per 1004.1.1. "Where an INTENDED use is not listed in Table 1004.1.1, the building official (not the brudgers) shall establish a use based on a listed use that most nearly resembles the intended use. Exception: Where approved by the building official, the actual number of occupants for whom each occupied space, floor or buildng is designed, although less than those determined by calculation, shall be permitted to be used in the determination of the design occupant load."brudgers said:What I find amazing about this thread is that some of the same people who get worried about bushes outside a bedroom window, will ignore a hundred and fifty people in an assembly occupancy.