Given:
Mixed Occupancy building; A-3 and S-1
Two story building but the top floor is much small than the bottom floor. The top floor is not a mezzanine.
Construction Type II-B
Fire suppression system throughout.
The bottom floor has A-3 & some S-1 areas, The S-1 areas as an aggregated total do not equate to more than 10% of the bottom floor’s area.
The top floor is totally S-1 and is under 3,000-sf. Therefore, I think this puts the second floor in the realm of Mixed Occupancy Separation and avoids accessible access to the upper floor. To avoid fire separation I feel that Section 508.3.2 Non-separated occupancies will be the method to use.
If it is a two story building why would Section 403 need to be reviewed?