Michael.L
I'm trying to determine the minimum width of a service corridor serving the "back of house" for two restaurants. This property is in a city that is currently operating under the 2015 International Building Code, although the building was constructed back in the 1980's.
The two restaurants are located in a ground-level indoor mall that has both retail and office spaces. The service corridor extends from the mall's ground-level loading/service dock to the central public space in the mall's interior. However, there is no public access to the service corridor (there is a combination lock on the door that connects the corridor to the public space) and it is not marked as an emergency exit. So the only persons with normal access to this service corridor are the staff of the two restaurants via the back doors from the restaurant's respective kitchen areas.
Restaurant #1 is large: it used to be two restaurant spaces that were combined into one. The total occupancy rating is 273. This restaurant shares an exterior wall of the building and the public has access to the restaurant via doors that open out to the exterior (private parking lot) and via doors that open into the mall's interior public space. This restaurant is counter service only with some outside seating; the majority of its space is occupied by kitchen, counter display, and storage. There are two back doors for staff into the service corridor.
Restaurant #2 is small. The total occupancy is 13. It is located entirely within the interior of the mall. This restaurant is also counter service only. Customers enter from the mall's interior public space via a pair of double doors. There is a single back door for staff into the service corridor.
For sizing the minimum corridor width and capacity, I believe I refer to 2015 IBC Section 1020.2. Table 1020.2 specifies a minimum width of 44 inches for "facilities not listed below" (none of which apply). However, Section 1020.2 also stipulates that the required capacity of corridors shall be determined as specified in Section 1005.1. There, we find that Section 1005.2.3 specifies that the capacity, in inches, shall be calculated by multiplying the occupant load served by a "means of egress capacity factor" of 0.2 inch per occupant. An exception is made that allows the use of an egress capacity factor of 0.15 inch per occupant in buildings equipped with automatic sprinkler systems and "an emergency voice/alarm communication system in accordance with Section 907.5.2.2." This building does have an automatic sprinkler system, but the fire alarm system is siren/horn only; no voice announcement system (I believe the building is grandfathered under a an older building code). In any case, I suspect the 0.15 inch per occupant capacity factor cannot be used.
My first question is, what number must I use for the "occupant load served by the means of egress." Do I use the total combined occupant loads of the two spaces (273 + 13) even though restaurant customers cannot normally get to this service corridor? If I were to use the total combined occupant loads, then 286 occupants multiplied by 0.2 inch per occupant would mean the minimum corridor width requirement would be 57.2 inches. Is this correct?
At this point, you're probably wondering why I want to calculate the minimum corridor width and capacity since the building (and corridor) is already built and both restaurants were approved by the city's Building Department and have been built-out and operating for well over a year. The reason is, when the owners of these two restaurants signed their leases (at about the same time), they were both told by the previous property owner that they could set up storage shelving in the service corridor along one wall. However, the new property owner recently sent an email to all the tenants instructing them to remove everything from the service corridor to allow emergency egress. Part of the problem is that employees of restaurant #1 were piling bags of trash in the clear area of the service corridor throughout the day. Also, some of their kitchen staff would eat meals in the corridor and leave chairs and junk in the service corridor's clear area. Because of their messiness, the new owners told everyone to clean out and remove everything, which was an overreaction IMO.
The service corridor width is 95 inches, but with the shelving in place, the available clear width without obstruction is 58.5 inches. So I believe that, even when using the total combined occupant loads, this clear width is acceptable and meets code requirements (assuming the employees of restaurant #1 are made to clean up their act).
To back up my assessment, I found a PDF document listed as "IBC Interpretation 06-11" (based on the 2009 IBC) that had the following Q & A:
Q: Are combustible, nonhazardous items such as tables, chairs, vending machines, furnishings, fixtures, displays,
etc. permitted to be located within an exit access corridor provided the minimum width of the exit access corridor is
maintained?
A: Yes. Sections 1005.1 and 1018.2 specify the required minimum width for corridors. If this clear width is available
without obstruction, design is acceptable in accordance with Section 1018.3. An obstruction to egress travel is not
created unless an object is placed or located within the required egress width.
My second question is, am I correct in determining that 58.5 inches of clear width meet the code requirements for means of egress?
maintained?