Thank you! agree! and this is how I've done it, (entire floor as B) but I was stumped about the request.Sum and then round up is how I have always done it for the entire floor. Basically when you are doing a room by room calculation it is a net calculation versus a gross calculation. If the entire floor is a "B" occupancy and you calculate the entire floor at 100 sq ft per person you will probably not exceed the sum of all occupiable spaces when adding up all the fractional amounts' and then rounding up to the next whole number.
[BE] FLOOR AREA, GROSS. The floor area within the inside perimeter of the exterior walls of the building under consideration, exclusive of vent shafts and courts, without deduction for corridors, stairways, ramps, closets, the thickness of interior walls, columns or other features. The floor area of a building, or portion thereof, not provided with surrounding exterior walls shall be the usable area under the horizontal projection of the roof or floor above. The gross floor area shall not include shafts with no openings or interior courts.
[BE] FLOOR AREA, NET. The actual occupied area not including unoccupied accessory areas such as corridors, stairways, ramps, toilet rooms, mechanical rooms and closets.
It was in particular regarding a "B" occupancy with a Conf. Room, (accessory only 200 sf) and a couple of other areas like that (a small exercise room and a lounge room) so first it was that each room's use is different, so I couldn't classify them as B. I had to calculate load (based on use) individually (fine, I get that even though I didn't think it was necessary but what do I know?!....)
Then, came the rounding up for each, which was news to me based on how I had have done it...(currently using IBC 2018) If I calculate the load based on use for each room, I end up with fractions (like Conf. Rm would be 13.33) so rounding up each and then rounding up again puts me over 49...
Maybe I need a chat with the AHJ