• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Occupant load for gym

SCBO1

Platinum Member
Joined
Oct 28, 2009
Messages
4,347
Location
MID WEST
I have a question in regards to the occupant load posting for a gym. Architect shows the OL including bleachers and standing room for a gym as one figure. And shows another OL for removable seats with another calculation. The signage is to be posted for the room at the exit. The gym has an upper floor to it so do you add the two calce for an overall OL or do you split the figure and post at each floor. Any rule to thumb on this?
 
Does the upper floor egress through the lower floor of the gym, or does the upper floor have its own separate means of egress?
 
The upper floor has its own exits but merges with a commons area that's use for a cafeteria which has its own OL calc to be posted.
 
The MOE for each space is designed for that OL.

Yes, once they are headed to the public way, the MOE is to be designed for all contributing OL's.
 