• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Oil supply line protection/ securing?

steveray

SAWHORSE
Joined
Nov 25, 2009
Messages
11,751
Location
West of the river CT
With these 2 sections, what is everyone requiring? Laying on the floor is "supported.".....If it is routed in the corner it is (or may not be) likely to be damaged. just saw one with about 20' not even fastened and it gave me pause.....Don't know if I can call it plumbing and say every 6' fastened, but maybe.... A little concerned that something or someone gets caught on it and yanks it across the room and breaks it....

M2203.1 General. Piping shall be installed in a manner to
avoid placing stresses on the piping, and to accommodate
expansion and contraction of the piping system.
M2203.2 Supply piping. Supply piping used in the installation
of oil burners and appliances shall be not smaller than 3/8-
inch (9 mm) pipe or 3/8-inch (9 mm) outside diameter tubing.
Copper tubing and fittings shall be a minimum of Type L.
 
$ ~ $

Section M1301.1 - Scope [ in the `15 IRC ] allows one to refer to
the IMC & the IFGC for more specific requirements.

I could only find Section 1305.2 [ from the `15 IMC ] - Protection
of pipe, equipment and appliance.........."Fuel oil pipe, equipment

and appliances shall be protected from physical damage".


The Code Official has the authority to render their interpretation
of this Code... " [ from Section 104.1 - General, `15 IRC ].

IMO, ...the Code Official has the [ legal ] authority to require
approved methods of securing the oil piping to the concrete flooring,
to prevent movement \ displacement \ trip hazard \ damage to the
piping.


$ ~ $
 