I think # 5 & 7 answers your question.
PLUS:::
7.1.3.2.2 An exit enclosure shall provide a continuous protected path of travel to an exit discharge.
Paragraph 7.1.3.2.2 emphasizes that exit enclosures, and the protection they afford the occupants, must be continuous. It is a fundamental premise that, once an occupant has been provided the level of protection afforded by an exit, that level of protection must be maintained to the exit discharge.
Paragraph 7.1.3.2.2 prohibits an exit stair or exit ramp arrangement that requires a person to leave the exit enclosure, become exposed to conditions on a floor, and then re-enter the exit enclosure to continue moving to the exit discharge. Exhibit 7.8 shows an unacceptable arrangement. The discontinuity of leaving the stair enclosure, and then re-entering the stair enclosure to continue moving to the level of exit discharge, creates too great a potential for exposing occupants to danger and blocking their egress route.
30.2.4.3 Reserved.
30.2.4.4 A single exit shall be permitted in buildings where the total number of stories does not exceed four, provided that all of the following conditions are met:
(1)
There are four or fewer dwelling units per story.
(2)
The building is protected throughout by an approved, supervised automatic sprinkler system in accordance with 30.3.5.
(3)
The exit stairway does not serve more than one-half story below the level of exit discharge.
(4)
The travel distance from the entrance door of any dwelling unit to an exit does not exceed 35 ft (10.7 m).
(5)
The exit stairway is completely enclosed or separated from the rest of the building by barriers having a minimum 1-hour fire resistance rating.
(6)
All openings between the exit stairway enclosure and the building are protected with self-closing door assemblies having a minimum 1-hour fire protection rating.
(7)
All corridors serving as access to exits have a minimum 1-hour fire resistance rating.
(8)
Horizontal and vertical separation having a minimum ½-hour fire resistance rating is provided between dwelling units