Trying to solve an issue on my apartment project regarding exterior stairs with open-ended corridors.
2018 IBC. Construction Type V-A, Group R-2. Four stories. NFPA 13 sprinkler system.
The building plan is very simple. Double loaded corridor with a stair at each end. No change of direction in the corridor.
It appears from Section 1027.6, exception 3 that no separation is required between the stairs and the open-ended corridor.
The corridors are 1-hour rated, so my assumption is that the 1-hour rating would also apply to the stair itself.
Normally an interior exit stair would have a 2-hour rated enclosure for 4 stories, but this is an exterior stair by definition, and I do not see any requirement in Section 1027 that addresses the rated walls at the stair in this situation.
Also, it does not make sense to me that the rating at the stair would be higher than the corridor if there is no separation between the two.
Wondering if anyone has dealt with this issue before?
2018 IBC. Construction Type V-A, Group R-2. Four stories. NFPA 13 sprinkler system.
The building plan is very simple. Double loaded corridor with a stair at each end. No change of direction in the corridor.
It appears from Section 1027.6, exception 3 that no separation is required between the stairs and the open-ended corridor.
The corridors are 1-hour rated, so my assumption is that the 1-hour rating would also apply to the stair itself.
Normally an interior exit stair would have a 2-hour rated enclosure for 4 stories, but this is an exterior stair by definition, and I do not see any requirement in Section 1027 that addresses the rated walls at the stair in this situation.
Also, it does not make sense to me that the rating at the stair would be higher than the corridor if there is no separation between the two.
Wondering if anyone has dealt with this issue before?