• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Open Stair as Egress

jl3

Registered User
Joined
Jun 4, 2020
Messages
14
Location
Denver, CO
Hi All,

We have an office building, B occupancy, under IBC 2018, fully sprinklered, 3 stories, about 30k SF per floor with under 250 occupants per floor. We're providing 2 egress stairs, one that would be enclosed, but were wondering if the other stair could be "open" between the 3 floors. Provided that the travel distance was under 300' per table 1017.2 from a remote corner of the 3rd level to the exterior doors at the entry lobby, would we be good?
 
No. Refer to Section 1006.3.1, which allows the path of travel to an exit to pass through no more than one story.

You can have an unenclosed exit access stairway from the 3rd story to the 2nd story that leads to an exit stair on the 2nd story (but not the same stair that provides the enclosed exit from the 3rd story).

Another option is to provide two enclosed exit stairs and one unenclosed stairway connecting all three stories complying with Section 1019.3, condition 4.
 
Stairs in Atriums are not "Exit access stairways", you would need to add an additional complying stair, or, as Ron pointed out "... provide two enclosed exit stairs and one unenclosed stairway connecting all three stories complying with Section 1019.3, condition 4...."
 
Stairs in Atriums are not "Exit access stairways", you would need to add an additional complying stair, or, as Ron pointed out "... provide two enclosed exit stairs and one unenclosed stairway connecting all three stories complying with Section 1019.3, condition 4...."
Actually, an atrium stair can be an exit stairway as added in the 2015 IBC, Section 1023.2, Exception 2. However, what is not clearly stated is that the atrium stair must comply with all other requirements for interior exit stairways (e.g., identification signs, standpipes at intermediate landings, etc.).
 