Open Web Wood Trusses in Commercial Construction
architect629
Philadelphia
My firm does interior fit out projects in the North East. We typically work with buildings of non-combustible construction, but we've run across a project recently that is constructed with open web wood roof trusses. I haven't had the pleasure of working with this type of construction (aside from residential) in my 15+ year career. I'm being told things by contractors bidding the projects that are "typical of this type of construction", that I'm not seeing in the code.
Here's some info about the project.
Type 5B construction, roughly 10,000 s.f.
Fully sprinklered, in both the attic and occupied space.
B occupancy with a large (>10% of floor area) storage function (S-2) which requires separation by a one hour fire barrier
Under 2012 IBC
I've been told by contractors that we need to install a layer of drywall on the underside of the existing wood roof trusses. I believe there's a requirement in the IRC to cover floor & roof framing, but I don't see anything in the IBC. The only thing I potentially see in the IBC is the fire blocking section. Would we need to create a fire block across the underside of the entire attic?
The contractors are also asking if they can stop the rated partitions at the underside of the roof trusses (which would have a layer of drywall on them). This is apparently "typical". Per the IBC a fire barrier is to be continuous from the slab to the underside of the sheathing. Even if you added drywall to the underside of the truss and created a one hour rated roof assembly, the fire barrier would need to extend to the sheathing. Am I missing anything?
Why are the partitions rated? In a sprinklered 1 story VB building, nothing is likely to be required to be rated....
Don't ask me why as it makes no sense to me, but IBC allows "exits" to stop at a lid, but not other FB....
4. Interior exit stairway and ramp enclosures required
by Section 1022.2 and exit access stairway and ramp
enclosures required by Section 1009.3 shall be permitted
to terminate at a top enclosure complying
with Section 713.12.
Not that it helps, but in Canada, all fire rated walls can terminate at a rated ceiling provided it has the same or greater rating.
With a sprinklered attic this does not scare me. What I am seeing now is we can build a 3 story VB apartment building with one exit stair with an unsprinklered attic over it. If the fire ends up in the attic (grill vs. siding and roof vents), it all falls in and no one gets out
If you have proper fire dampers and fire stopping, the only way you can have a fire would be electrical in nature. Our code also requires concealed spaces to be fire blocked into certain size areas that will prevent fire spread throughout the concealed space simultaneously. If the designer chooses not to sprinkler the concealed space per NFPA 13R, the concealed space limits get smaller to account for the increase in hazard.
TM...I've seen it on houses where the unattended grill lights the vinyl siding on fire, up into the soffit vent, and then the attic is on fire before anyone even knows there is a problem...HOPEFULLY management can control this in apartments, but I am skeptical....
I think your skepticism is well placed. Our code recently started permitting mid rise combustible construction for residential and business and personal services occupancies. One of the requirements is for all balconies to be protected by sprinklers.
This has also happened at several apartments in the Richmond area.
Under 2012 IBC
""""""The contractors are also asking if they can stop the rated partitions at the underside of the roof trusses (which would have a layer of drywall on them). This is apparently "typical". Per the IBC a fire barrier is to be continuous from the slab to the underside of the sheathing. Even if you added drywall to the underside of the truss and created a one hour rated roof assembly, the fire barrier would need to extend to the sheathing. Am I missing anything? """"""
Not an IBC person
But I normally see four feet out from the rated wall, sheetrock attached to the roof deck