• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Option For Roof Deck Coverings Residential Removed from FBC 2023 - [Change in Building Code]

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,055
Location
Somewhere Too Hot & Humid
Here is the verbiage for 2023: As you can see, some options were removed.

REQUIREMENTS FOR ROOF COVERINGS​

R905.1Roof covering application.​

Roof coverings shall be applied in accordance with the applicable provisions of this section and the manufacturer’s installation instructions. Unless otherwise specified in this section, roof coverings shall be installed to resist the component and cladding loads specified in Table R301.2(2), adjusted for height and exposure in accordance with Table R301.2(3).

R905.1.1Underlayment.​

Underlayment for roof slopes 2:12 and greater shall conform to the applicable standards listed in this chapter. Underlayment materials required to comply with ASTM D226, D1970, D4869, D6757, or ASTM D8257, shall bear a label indicating compliance to the standard designation and, if applicable, type classification indicated. Underlayment for roof slopes 2:12 and greater shall be applied and attached in accordance withSection R905.1.1.1 or R905.1.1.2 as applicable.
Exception: Compliance with Section R905.1.1.1 is not required for structural metal panels that do not require a substrate or underlayment.
Table R905.1.1(1) Underlayment Types. Reserved.
Table R905.1.1(2) Underlayment Application. Reserved.
Table R905.1.1(3) Underlayment Attachment. Reserved.

R905.1.1.1Underlayment for asphalt shingles, metal roof panels or shingles, mineral surfaced roll roofing, slate and slate-type shingles, wood shakes and wood shingles.​

Underlayment for asphalt shingles, metal roof panels or shingles, mineral surfaced roll roofing, slate and slate-type shingles, wood shakes and wood shingles shall comply with one of the following methods:
  1. 1.The entire roof deck shall be covered with an approved self-adhering polymer-modified bitumen underlayment complying with ASTM D1970 installed in accordance with both the underlayment manufacturer’s and roof covering manufacturer’s installation instructions for the deck material, roof ventilation configuration and climate exposure for the roof covering to be installed.
    Exceptions:
    1. 1.This method is not permitted for wood shingles or shakes.
    2. 2.An existing self-adhering modified bitumen underlayment that has been previously installed over the roof decking and, where it is required, renailing off the roof sheathing in accordance with Section 706.7.1 of the Florida Building Code, Existing Building can be confirmed or verified. An approved underlayment in accordance with Table R905.1.1.1 for the applicable roof covering shall be applied over the entire roof over the existing self-adhered modified bitumen underlayment.
  2. 2.A minimum 33/4-inch-wide (95 mm) strip of self-adhering polymer-modified bitumen membrane complying with ASTM D1970 or self-adhering flexible flashing tape complying with AAMA 711, Level 3 [for exposure up to 176°F (80°C)], installed in accordance with the manufacturer’s instructions for the deck material, shall be applied over all joints in the roof decking. An approved underlayment in accordance with Table R905.1.1.1 for the applicable roof covering shall be applied over the entire roof over the membrane strips.
  3. 3.Two layers of ASTM D226 Type II, ASTM D4869 Type III or Type IV or ASTM D8257 underlayment shall be installed as follows: Apply a strip of underlayment for the first course that is half the width of a full sheet parallel to and starting at the eaves, fastened sufficiently to hold in place. Starting at the eave, apply a full sheet of underlayment, for the second course. Apply the third course of underlayment overlapping the second course half the width of a full sheet plus 2 inches (51 mm). Overlap all successive courses half the width of a full sheet plus 1 inch (25 mm). End laps shall be 6 inches (152 mm) and shall be offset by 6 feet (1829 mm). Underlayment shall be attached to a nailable deck with corrosion- resistant fasteners with a maximum fastener spacing, measured horizontally and vertically, of 12 inches (305 mm) o.c. between side laps, and one row at the end and side laps fastened 6 inches (152 mm) o.c. Underlayment shall be attached using annular ring or deformed shank nails with metal or plastic caps with a nominal cap diameter of not less than 1 inch (25 mm). Metal caps are required where the ultimate design wind speed, Vult, equals or exceeds 170 mph. Metal caps shall have a thickness of not less than 32-gage sheet metal. The minimum thickness of the outside edge of plastic caps shall be 0.035 inch (0.889 mm). The cap nail shank shall be not less than 0.083 inch (2.1082 mm) for ring shank nails. The cap nail shank shall have a length sufficient to penetrate through the roof sheathing or not less than 3/4 inch into the roof sheathing.
Exception: Use of ASTM D8257 underlayment is not permitted for wood shingles or shakes.

HERE IS WHAT WAS IN 2020: (next post due to character limitation)
 
2020 Options Here:

R905.1.1.1Underlayment for asphalt, metal, mineral surfaced, slate and slate-type roof coverings.​

Underlayment for asphalt shingles, metal roof shingles, mineral surfaced roll roofing, slate and slate-type shingles, and metal roof panels shall comply with one of the following methods:

  1. 1.The entire roof deck shall be covered with an approved self-adhering polymer-modified bitumen underlayment complying with ASTM D1970 installed in accordance with both the underlayment manufacturer’s and roof covering manufacturer’s installation instructions for the deck material, roof ventilation configuration and climate exposure for the roof covering to be installed.
    Exception: An existing self-adhering modified bitumen underlayment that has been previously installed over the roof decking and where it is required, renailing off the roof sheathing in accordance with Section R908.7.1 can be confirmed or verified. An approved underlayment in accordance with Table R905.1.1.1 for the applicable roof covering shall be applied over the entire roof over the existing self-adhered modified bitumen underlayment.
  2. 2.A minimum 4-inch-wide (102 mm) strip of self-adhering polymer-modified bitumen membrane complying with ASTM D1970, installed in accordance with the manufacturer’s instructions for the deck material, shall be applied over all joints in the roof decking. An approved underlayment in accordance with Table R905.1.1.1 for the applicable roof covering shall be applied over the entire roof over the 4-inch-wide (102 mm) membrane strips.
    Exception: A synthetic underlayment that is approved as an alternative to underlayment complying with ASTM D226 Type II and having a minimum tear strength of 15 lbf in accordance with ASTM D4533 and a minimum tensile strength of 20 lbf/inch in accordance with ASTM D5035 shall be permitted to be applied over the entire roof over the 4-inch-wide (102 mm) membrane strips. This underlayment shall be installed and attached in accordance with the underlayment attachment methods of Table R905.1.1.1 for the applicable roof covering and slope and the underlayment manufacturer’s installation instructions.
  3. 3.A minimum 33/4-inch wide (96 mm) strip of self-adhering flexible flashing tape complying with AAMA 711, Level 3 [for exposure up to 176°F (80°C)], installed in accordance with the manufacturer’s instructions for the deck material, shall be applied over all joints in the roof decking. An approved underlayment in accordance with Table R905.1.1.1 for the applicable roof covering shall be applied over the entire roof over the 4-inch-wide (102 mm) flashing strips.
    Exception: A synthetic underlayment that is approved as an alternative to underlayment complying with ASTM D226 Type II and having a minimum tear strength of 15 lbf in accordance with ASTM D4533 and a minimum tensile strength of 20 lbf/inch in accordance with ASTM D5035 shall be permitted to be applied over the entire roof over the 4-inch-wide (102 mm) flashing strips. This underlayment shall be installed and attached in accordance with the underlayment attachment methods of Table R905.1.1.1 for the applicable roof covering and slope and the underlayment manufacturer’s installation instructions.
  4. 4.Two layers of ASTM D226 Type II or ASTM D4869 Type III or Type IV underlayment shall be installed as follows: Apply a 19-inch (483 mm) strip of underlayment felt parallel to and starting at the eaves, fastened sufficiently to hold in place. Starting at the eave, apply 36-inch-wide (914 mm) sheets of underlayment, overlapping successive sheets 19 inches (483 mm); end laps shall be 6 inches and shall be offset by 6 feet. The underlayment shall be attached to a nailable deck with corrosion-resistant fasteners with one row centered in the field of the sheet with a maximum fastener spacing of 12 inches (305 mm) o.c., and one row at the end and side laps fastened 6 inches (152 mm) o.c. Underlayment shall be attached using annular ring or deformed shank nails with metal or plastic caps with a nominal cap diameter of not less than 1 inch. Metal caps are required where the ultimate design wind speed, Vult, equals or exceeds 170 mph. Metal caps shall have a thickness of not less than 32-gage sheet metal. Power-driven metal caps shall have a minimum thickness of 0.010 inch. Minimum thickness of the outside edge of plastic caps shall be 0.035 inch. The cap nail shank shall be not less than 0.083 inch for ring shank cap nails. Cap nail shank shall have a length sufficient to penetrate through the roof sheathing or not less than 3/4 inch into the roof sheathing.
  5. 5.Two layers of a reinforced synthetic underlayment that has a product approval as an alternative to underlayment complying with ASTM D226 Type II shall be permitted to be used. Synthetic underlayment shall have a minimum tear strength of 15 lbf in accordance with ASTM D4533 and a minimum tensile strength of 20 lbf/inch in accordance with ASTM D5035, and shall meet the liquid water transmission test of Section 8.6 of ASTM D4869. Synthetic underlayment shall be installed as follows: Apply a strip of synthetic underlayment that is half the width of a full sheet parallel to and starting at the eaves, fastened sufficiently to hold in place. Starting at the eave, apply full sheets of reinforced synthetic underlayment, overlapping successive sheets half the width of a full sheet plus the width of the manufacturer’s single-ply overlap. End laps shall be 6 inches and shall be offset by 6 feet. Synthetic underlayment shall be attached to a nailable deck with corrosion-resistant fasteners with a maximum fastener spacing, measured horizontally and vertically, of 12 inches (305 mm) o.c. between side laps, and one row at the end and side laps fastened 6 inches (152 mm) o.c. Synthetic underlayment shall be attached using annular ring or deformed shank nails with metal or plastic caps with a nominal cap diameter of not less than 1 inch. Metal caps are required where the ultimate design wind speed, Vult, equals or exceeds 170 mph. Metal caps shall have a thickness of not less than 32-gage sheet metal. Power-driven metal caps shall have a minimum thickness of 0.010 inch. Minimum thickness of the outside edge of plastic caps shall be 0.035 inch. The cap nail shank shall be not less than 0.083 inch for ring shank cap nails. Cap nail shank shall have a length sufficient to penetrate through the roof sheathing or not less than 3/4 inch into the roof sheathing.
 