Osha Ship Ladder Code
Cadkiller
Bergenfield, NJ
Hi Group,
I have detailed a few ships ladders with a 4" tread and a 7" riser, to have the owner request that it be replaced. I have tried to explain to OSHA that this combination is very awkward/dangerous to walk down facing forward and also awkward to walk up as it requires you to take baby steps. The design team is drawing them this way because of the current codes, not knowing that they are awkward/dangerous IMO. I have attached an image of one of them which wasn't replaced and remains as is. I could only imagine how many other projects have been designed and built like this.
Osha's reply is as follows.
Please note that the requirements for ship stairs in 29 CFR 1910.25 are consistent with ANSI/ASSE A1264.1-2007, Safety Requirements for Workplace Walking/Working Surfaces and Their Access,’ Workplace, Floor, Wall, and Floor Openings,‘ Stairs and Guardrail
Systems.
Additionally, § 1910.25(b)(8) requires employers to ensure that ship stairs “are used only when the employer can demonstrate that it is not feasible to provide standard stairs.”
Specific requirements for ship stairs are located at 29 CFR 1910.25(e). Paragraph (e)(2) requires that ship stairs have open risers with a vertical rise between tread surfaces of 6.5 to 12 inches (17 to 30 cm). OSHA believes that the tread depths provided in 1910.25(e) do not pose hazards when ship stairs are used, as the open risers on these stairs would give an additional space for the foot when needed.
Finally, to change these requirements, OSHA would need to conduct notice-and-comment rulemaking. OSHA does not currently plan to conduct rulemaking on 29 CFR 1910.25, but should the agency do so in the fixture, we will evaluate the dimension requirements for ship stair riser heights and tread depths as part of the rulemaking.
Let me know your thoughts regarding this.
Sincerely,
Ed B
Does OSHA require 4" tread or 4" minimum? I think 5 or 6 is better. And why not go to maximum 12" rise? I also push towards the minimum 50° and rarely above 60°.
I'd find the 7" riser tough.
In my planning work (catwalks and such over stages and auditoriums) I actually prefer straight ladders to ships ladders and just detest the alternating tread devices. You can't carry a light or toolbox on any of them safely.
Bill,
Typically I try and use a 6" tread with a 9" riser
Bill,
OSHA requires a 4" minimum tread depth with 6 1/2" to 12" riser height.
They also show ship ladders between 50 to 70 degrees.
Most ships ladders I've climbed or seen have been closer to 12" risers, starting with high school and college lighting/projection rooms in 1960s/early 1970s.
"They also show ship ladders between 50 to 70 degrees."
Is that a recent change? I was taught that nothing could be between 50 to 70 deg.
Just for fun, IBC ship ladders:
1011.15.1Handrails of ship’s ladders.
Handrails shall be provided on both sides of ship’s ladders.
1011.15.2Treads of ship’s ladders.
Ship’s ladders shall have a minimum tread depth of 5 inches (127 mm). The tread shall be projected such that the total of the tread depth plus the nosing projection is not less than 8 1/2 inches (216 mm). The maximum riser height shall be 9 1/2 inches (241 mm).
Can anyone interpret that minimum 5" plus nosing projection not less than 8 1/2"? 3 1/2" nosing projection? Required?
What rules does everyone follow...IBC or OSHA? They seem to be conflicting.
I don't think an IBC ship's stair conflicts with the OSHA requirements. OSHA allows risers between 6.5" and 12". The IBC limits risers to 9.5", with no minimum. No conflict there. OSHA requires a minimum tread depth of 4". The IBC requires a minimum tread depth of 5". No conflict there.
If there is a conflict -- as a licensed building official, my duty is to enforce the IBC (as amended by my state). I don't enforce OSHA.