I think it is comply with #1 or ....2 and 3.....The way I read it, the requirements of #s 1 and 2 are met. However, if you wish to place outlet boxes on opposite sides of a vertical fire separation, you need to meet #3, as these requirements are in addition to #s 1 and 2. Am I crazy?
Out of curiosity, how do the American codes speak to this?
Pads are a fire stop, not a fire block.Pads <> fire block in this instance. I'd accept "bulkheading" one of the outlets with F/R drywall, though.
Pads are a fire stop, not a fire block.
I put in an interpretation request, I will try to remember to post the answer here when it comes in, which could be months away.
If the rating is derived from the membrane only, that would be acceptable. But, when an assembly approach is used, I don't think there would be justification in the code for it.I have seen sheetrock boxes build around recessed assemblies, would the gallery accept this method?
I have seen sheetrock boxes build around recessed assemblies, would the gallery accept this method?
If the rating is derived from the membrane only, that would be acceptable. But, when an assembly approach is used, I don't think there would be justification in the code for it.
1023.5 Penetrations. Penetrations into or through interior exit
stairways and ramps are prohibited except for the following:
1. Equipment and ductwork necessary for independent
ventilation or pressurization.
2. Fire protection systems.
3. Security systems.
4. Two-way communication systems.
5. Electrical raceway for fire department communication
systems.
6. Electrical raceway serving the interior exit stairway
and ramp and terminating at a steel box not exceeding
16 square inches (0.010 m2).
7. Structural elements supporting the interior exit stairway
or ramp or enclosure, such as beams or joists.
Such penetrations shall be protected in accordance with
Section 714. There shall not be penetrations or communication
openings, whether protected or not, between adjacent interior
exit stairways and ramps.
Exception: Membrane penetrations shall be permitted on
the outside of the interior exit stairway and ramp. Such
penetrations shall be protected in accordance with Section
714.4.2.
Sorry, I thought we were still discussing general allowances, not my foray into exits.From Chapter 10 of the IBC:
As section 1023.5 states in the opening sentence, there are two types of penetrations: through penetrations (from whatever is outside the exit enclosure all the way through the wall and into the exit), and membrane penetrations (through one side of the enclosure wall into the wall cavity). Neither through penetrations nor membrane penetrations are allowed unless they are for equipment that serves the exit -- except that membrane penetrations ARE allowed if protected per IBC 714.4.2.
You'll get limited mileage (kilometerage?) out of IBC references in Canada.
Our favorite answer: it depends.Does the CBC have a different distinction between membrane penetrations and through penetrations? Item #1 in the code section you reproduced specifically addresses membrane penetrations, so I suspect the concept is the same on both side of the border.