RLGA
SAWHORSE
I'm entering new territory regarding medical gases. I have a Group I-1 assisted living facility that will have a medical oxygen system for a portion of the building. I have determined that the quantity in storage and in use will be well over the 3,000 cu. ft. permitted per Table 307.1(1) (twice the allowable since a sprinkler system is installed).
The issue is that the bulk of the oxygen system's quantity is in storage outside and the only portion of the system that is inside the building is the distribution piping to the outlets in the rooms, which, in all likelihood is less than 3,000 cu. ft.. For outdoor storage, the IFC and NFPA 99 have no restrictions on the quantity of oxygen storage or use, which is fine. But, when considering the quantity applicable to a control area for the interior of the building, do I only use that portion that is actually contained within the building, or must I consider the entire system, even though most of the quantity is outdoors?
Thanks.
The issue is that the bulk of the oxygen system's quantity is in storage outside and the only portion of the system that is inside the building is the distribution piping to the outlets in the rooms, which, in all likelihood is less than 3,000 cu. ft.. For outdoor storage, the IFC and NFPA 99 have no restrictions on the quantity of oxygen storage or use, which is fine. But, when considering the quantity applicable to a control area for the interior of the building, do I only use that portion that is actually contained within the building, or must I consider the entire system, even though most of the quantity is outdoors?
Thanks.