Rick18071,
Was the house constructed at the local tech school, issued a C. of O.?
If not, then it is not a legally recognized SFD. It would need to be inspected &
approved to the standards under which it was constructed, and approved by
the AHJ in which it is installed.
If that AHJ determines it is a Property Maintenance issue, then Section 604.3
[ might ] apply.....From the 2006 IPMC,....Section 604.3 - "Electrical system hazards.
Where it is found that the electrical system in a structure constitutes a hazard
to the occupants or the structure by reason of inadequate service, improper
fusing, insufficient receptacle and lighting outlets, improper wiring or installation,
deterioration or damage, or for similar reasons, the code official shall require
the defects to be corrected to eliminate the hazard."
It sounds as though they need to move the panel.
Also, I do not believe that signage would satisfy the intent or the letter for the
safety of the occupants.....That would also let the Tech school off the hook!
& & & &