There are some changes in the 2017 National Electrical Code with regard to rooms that require doors to have panic hardware or fire exit hardware. Since the NEC is not one of the codes I spend a lot of time reading, I'm hoping y'all can help me confirm whether I'm interpreting this correctly (or not).
Previous Edition:
The 2014 edition requires outswinging doors with listed panic hardware for doors intended for entrance/egress and located within 25 feet of the required working space, where any of the following are true:
New Edition:
In the 2017 edition, outswinging doors with listed panic hardware are required for doors intended for entrance/egress and located within 25 feet of the required working space, where any of the following are true:
* The NEC also requires these doors to be kept locked, with access allowed only to qualified persons.
Did I miss anything? Do any of you have insight into why the voltage limit went from 600 volts to 1000 volts? That seems like a pretty big jump.
Thanks in advance for your help!
Previous Edition:
The 2014 edition requires outswinging doors with listed panic hardware for doors intended for entrance/egress and located within 25 feet of the required working space, where any of the following are true:
- Where equipment is 600 volts or less and 800 amps or more and contains overcurrent devices, switching devices, or control devices (110.26 (C) (3))
- Where equipment is 600 volts or more (110.33 (A) (3))*
- Battery rooms (480.9 (E))
New Edition:
In the 2017 edition, outswinging doors with listed panic hardware are required for doors intended for entrance/egress and located within 25 feet of the required working space, where any of the following are true:
- Where equipment is 1000 volts or less and 800 amps or more and contains overcurrent devices, switching devices, or control devices (110.26 (C) (3))
- Where equipment is 1000 volts or more (110.33 (A) (3))*
- Transformer vaults (450.43 (C))*
- Battery rooms (480.10 (E))
- Energy storage systems (706.10 (D))
* The NEC also requires these doors to be kept locked, with access allowed only to qualified persons.
Did I miss anything? Do any of you have insight into why the voltage limit went from 600 volts to 1000 volts? That seems like a pretty big jump.
Thanks in advance for your help!