LGreene
1008.1.10.1 Installation. Where panic or fire exit hardware is installed, it shall comply with the following:
1. Panic hardware shall be listed in accordance with UL 305;
2. Fire exit hardware shall be listed in accordance with UL 10C and UL 305;
3. The actuating portion of the releasing device shall extend at least one-half of the door leaf width; and
4. The maximum unlatching force shall not exceed 15 pounds (67 N).
Which is the intent of item 3 above?
a) The length of the actuating portion (typically a touchpad or crossbar) must measure at least half of the measurement of the door width - ie. the actuating portion for a 3'-wide door must be at least 18", for a 3'-6" wide door must be at least 21".
b) The end of the actuating portion must extend at least to the half-way point of the door width - ie. if the actuating portion is 18" long, and begins 4" in from the lock edge, the other end of the actuating portion would reach to a point 22" across the door and would therefore accommodate a 44"-wide door.